mango1952-ga,
From the following websites we get the Poiseulle equation for laminar
flow in a pipe :
http://landau1.phys.virginia.edu/classes/241L/poise/poise.htm
http://www-unix.oit.umass.edu/~phys131f/11_18.pdf (gives info about mu
for water)
pi * Dp * r^4
F = ------------
8 * mu * l
F = volume of flow per unit time
pi = 3.14159...
Dp = change in pressure at either end of pipe
r = radius of pipe
mu = coefficient of viscosity
l = length of pipe
In general we assume that mu for water is 1 x 10^-3 = 0.001.
For the 10m pipe, we have :
l = 10m
r = 20mm = 0.02m
The pump has :
F = 250 l/min = 4.1667 l/sec = 0.004167 m³/sec
So using the poiseulle equation we get:
3.14159 * Dp * 0.02^4
0.004167 = ---------------------
8 * 0.001 * 10
So Dp = 0.004167 * 8 * 0.001 * 10 / (3.14159 * 0.02^4)
= 663.146 g/m²
= 663.146 / 6890 = 0.1 psi (approx)
So the pressure at the outlet will be 76 - 0.1 = 75.9psi
The volume of the pool is 25m x 12m x 1.5m = 450m³
At a rate of .25m³/min, it would take 450/.25 = 1800 minutes = 30
hours
to empty the pool.
For the 20m pipe, we have :
l = 20m
r = 12.5mm = 0.0125m
So Dp = 0.004167 * 8 * 0.001 * 20 / (3.14159 * 0.0125^4)
= 8691 g/m²
= 8691 / 6890 = 1.26 psi (approx)
The final pressure will still be 76 - 1.26 psi = 74.74 psi, which
still seems suitable.
A good example of the difference between laminar and turbulent flow is
given at the bottom of the following site :
http://www.uvi.edu/Physics/SCI3xxWeb/Plumbing/FluidDynamics.html
As you can see, laminar flow requires that all flow is parallel to the
sides of the pipe (the Poisseuile equation requires a horizontal pipe
- this may not be the case for fighting a fire). In general this
should be a good approximation - however you will not have laminar
flow :
1) at the connection to the pump
2) at curves or kinks in the hose
3) at the open end of the hose
The effect of these should be minimal.
I had to make a few assumptions to answer your question. The first was
to ignore the effect of getting the water from the bottom of the pool.
If this is the case, then you need to reduce the pressure by :
delta P = rho*g*deltaH = (approx) 9800 * 1.5 = 2.14 psi
Let me know if you have any further concerns and I will do my best to
address them.
Regards
calebu2-ga