Subject:
Humidity calculations
Category: Science > Earth Sciences Asked by: yanos-ga List Price: $100.00 |
Posted:
31 Jan 2004 06:32 PST
Expires: 02 Feb 2004 09:04 PST Question ID: 302108 |
I need a set of equations or source code (VB) to calculate the humidity of air as follows: 1. Input Temperature (dry bulb), pressure and relative humidity and get out specific humidity in grains water/pound dry air. 2. Input Dry bulb temperature, wet bulb temperature and pressure and get out relative humidity %. 3. Other related calculations if available. | |
| |
| |
| |
|
![]() | ||
|
There is no answer at this time. |
![]() | ||
|
Subject:
Re: Humidity calculations
From: eiffel-ga on 31 Jan 2004 13:32 PST |
The required forumula and physical constants are clearly set out in NASA Technical Note TN D-8401 "Equations for the determination of humidity from Dewpoint and Psychrometric Data" http://www.dfrc.nasa.gov/DTRS/1977/PDF/H-937.pdf It would be difficult to type these equations as an answer without the risk of transcription errors or confusion due to reformatting as plain text, so I suggest you get them from that source. Additionally, you will have to convert from "pounds per cubic foot of air" to "grains per pound of air" (although the necessary constants are there for you). Your second formula is directly present in the referenced work, and you will have to back-substitute the formula for RH into the presented formula for absolute humidity, in order to obtain it from your starting points (dry bulb temp, pressure and relative humidity). Note also that different constants are needed depending on whether the wet bulb is at ice temperatures or water temperatures. These constants are clearly presented in the appendix of the referenced article. |
Subject:
Re: Humidity calculations
From: yanos-ga on 31 Jan 2004 15:08 PST |
For some reason the link freezes my browser. I will continue to try but pounds per cubic foot is a volumetric measure and grains per pound of air so I still need density at the specific temperature and pressure to get my required number. Any ideas on why the link doesn't work for me? |
Subject:
Re: Humidity calculations
From: pafalafa-ga on 31 Jan 2004 16:57 PST |
Hi yanos, I had a look at the link myself that eiffel found, and it's certainly jam-packed with formula, but I'm not sure it has everything you need for specific humidity calcs. Hopefully, Im mistaken, and it's all there. Try "saving" the link to your PC first and then opening it with Adobe (rather than opening it directly). That might help you avoid the freeze-up. pafalafa-ga |
Subject:
Re: Humidity calculations
From: yanos-ga on 31 Jan 2004 17:41 PST |
Thanks for the input and I was able to access the PDF file using the method suggested. The methods given, however, do not include finding Specific Humidity from Relative Humidity, temperature and pressure. I am beginning to think that perhaps it is more complicated than I thought. The initial link http://www.thunderscientific.com/humicalcpg/humicalc.html# did provide the functionality that I am looking for but the equations used in that do not appear to be in the reference document http://www.dfrc.nasa.gov/DTRS/1977/PDF/H-937.pdf. Perhaps I just do not have the background to translate the equations but then that is why I offered to pay someone to do it for me. (I am too lazy or too stupid I guess). |
Subject:
Re: Humidity calculations
From: yanos-ga on 31 Jan 2004 17:44 PST |
p.s. I have emailed humicalc and one other but I don't think I will get an answer back before I need it. I also don't know if they will sell the DLL or source code for a reasonable price. |
Subject:
Re: Humidity calculations
From: pafalafa-ga on 31 Jan 2004 18:59 PST |
I'm glad the pdf trick worked out. Wish I could help you in a more timely fashion, but I'm afraid it would take me too long to slog through the materials to even figure out if an answer were possible. If you want researchers to continue looking out for possibilities for you, you should make that clear in another clarification...otherwise, they might all suppose it's too late to answer your question. Best of luck. pafalafa-ga |
Subject:
Re: Humidity calculations
From: yanos-ga on 31 Jan 2004 21:54 PST |
Still looking for an answer on this one. |
Subject:
Re: Humidity calculations
From: eiffel-ga on 01 Feb 2004 02:29 PST |
Yanos, If you look at the equations on page 22 of the NASA report, you will see that the last one starts with U(T, T', p) and calculates the relative humidity from the dry bulb and wet bulb temperatures plus the air pressure. That's your second equation taken care of (just multiply by 100 to get it as a percentage). It's the first one that's difficult, because you want to get the specific humidity starting from RH, dry bulb temperature and pressure. Are you sure you can't start from dry bulb and wet bulb temperatures plus the air pressure, just as you did for your relative humidity calculation? If so, the fifth equation on page 22, starting with H(T, T', p), is exactly what you need, although you need to take it further to get it in grains per pound as you require. If you are stuck with RH, dry bulb temperature and pressure as your inputs, then you can still use the fifth equation, but first you have to calculate the wet bulb temperature from your inputs. To do this, you can manipulate the final equation to get T' on the left-hand-side. This gives you T' (wet bulb temperature) calculated from dry bulb temperature, relative humidity and pressure. You then have the inputs you need to use the fifth equation. Sorry, I don't trust myself to manipulate that final equation myself and get the right answer (it's too many years since I've used all the rules about manipulating powers and logarithms on equations as complex as this one), but I reckon that's the best approach. Finally, I don't know what level of accuracy you need, but if you're looking for an "easy way out" you could consider using the online calculators to produce a large table of results, and use table lookup instead of formulae in your computer program. |
Subject:
Re: Humidity calculations
From: majortom-ga on 01 Feb 2004 14:07 PST |
I have found answers for you, but I'm not usually a VB programmer, you need an answer right away, and I'm going out the door shortly. So instead of taking your $100 I'll just share my sources -- which are very straightforward code for exactly what you want, which happens to be in C and Javascript at the moment. But all three languages do ordinary algebra like this the same way -- this code is very close to VB already. * * * The following page offers simple C source code for step 1. It might look intimidating but it's just straightforward math code, and would look about the same in any language. You should have no trouble rephrasing it in Visual BASIC: Hot List for PTM Example Applications, U of Kentucky http://www.bae.uky.edu/~gates/psych/PTM_apps.htm And the specific C program for this task: http://www.bae.uky.edu/~gates/psych/PTM/dbrh2al.c This program also fulfills part 3 of your question by outputting several other interesting factors. * * * The following page offers straightforward Javascript code for step 2. This will be even easier to translate. Just go to the page and hit "view source:" Wet and Dry Bulb Calculator http://members.nuvox.net/~on.jwclymer/wet.html You should have no trouble completing the project in a hurry with this information, but if you really want me to translate it to VB for you when I'm back at my desk Monday morning, by all means let me know and I'd be glad to collect the $100 after all. |
Subject:
Re: Humidity calculations
From: yanos-ga on 01 Feb 2004 18:45 PST |
This is excellent thanks. I will get someone who knows C to compile it into a DLL for me and I am off to the races. Thanks very much. |