Hello ritaritz, I contacted Marley and they e-mailed a 2 page spec
sheet which is in a .pdf file (requires Adobe Reader). I also called
Marley (800)462-7539 and talked with Teresa. The "TY-12X" is the
crossflow product and the "TD-12C" is the counterflow version. Both
are furnished in 5.75 inch thickness X 9.6/12.2/24 inch widths X 144
inch length. Here is the text from the spec sheets:
Marley developed the first cellular drift eliminator over 20 years ago
when eliminator designs were primarily blade type configurations and
not very effective. Next, Marlet patented the XCEL generation of
eliminators in the early 80's. No other eliminator could come close to
XCEL eliminator's low drift rate and low pressure drop. Now, virtually
every eliminator is a nesting cellular PVC type design. Introducing
XCELplus, a more advanced design that meets or exceeds today's
demanding specifications for drift emissions, without sacrificing fan
horsepower. Now you can have drift rates half of the original XCEL
with equivalent pressure drop. The eliminator discharge angle is
important enough to warrant two seperate eliminator designs-one for
crossflow and one for counterflow towers. Tests show that the air
direction leaving the eliminator is extremely important-imperfect
designs create additional work for the fan. This means either
increased fan horsepower-or reduced cooling tower performance. The
crossflow version features drainage slots within the eliminator pack
to insure trapped drift is returned to the wet side of the cooling
tower. Low drift rate is the primary goal of eliminator design.
XCELplus boasts typical drift rates of .001% of the total GPM. Drift
rates of .0005% and lower are available depending on tower
configuration. Drift rates with the original XCEL elininator were so
low that a better measurement method than the Sensitive Paper
Technique was required. The Hot Bead Isokinetic Drift Measurement
(HBIK) method pionered by Marley over 20 years ago, is now the
endorsed CTI standard test procedure, ACT-140 for drift measurement
today. Considering low drift rates and low pressure drop, XCELplus is
the most effective cooling tower drift eliminator available in the
market place today.
SUGGESTED SPECIFICATION:
Drift eliminators shall be of cellular type, Marley XCELplus or
approved equal. The eliminators shall be thermoformed from 17 mil
(.017 inch) PVC (polyviny chloride) into a configuration providing at
least 3 changes in air direction and solvent welded into multiple
sheet packs. Eliminators used in crossflow towers must provide a
discharge angle (as defined by the last section of the eliminator
itself) of at least 42 degrees from the horizontal when installed. The
mass drift quantity, determined by the CTI Drift Test Code ACT-140
shall not exceed ____ % of the total GPM and shall be guranteed for
all operating conditions. The eliminator packs shall be able to span
66" unsupported for counter flow configurations and 72" for crossflow,
with minimal deflection at design conditions. Eliminators shall be FM
approved. Eliminator packs shall measure up to 24" wide, 5.75 in
depth, and up to 12'-0" long.
Sorry I can't show you the pictures here. You can contact Marley and
get the .pdf file like I did. I could e-mail the file to you, but it
is not wise to post your e-mail address here. Here is contact info for
Marley:
Marley Cooling Technologies
7401 W. 129 Street
Overland Park, Kansas 66213
(800)462-7539
www.marleyct.com
e-mail: info@marleyct.spx.com
Hope this is what you are looking for, Redhoss |