Plumbing problem.Fully pumped system. I have removed and then refitted
a radiator.Refilled system, bled all valves on radiators, pump and
pipe work. Boiler fires, heats up to temperature and then cuts out.
Press reset button when cool and it will fire again. Radiators do not
get warm. Pump is working and hot, as are pipes on both sides of
it.Presume I have an air lock somewhere, but cannot shift it. Have
repeated all the above several times.
Need help please. |
Clarification of Question by
raefa-ga
on
10 Jan 2005 17:16 PST
Thanks to answerfinder, not either of those suggestions.
Thanks guzzi, pipework system is about 20 years old with all
copper.All radiators & boiler have been replaced within last 6
years.System has been drained completely; drained with radiator valves
shut;drained with header tank not shut off until clean water flowing
and then drain plug closed.All combinations you suggest about bleading
radiators I have done.I have as from today one radiator, third on
system getting warm, first and second not quite cold, all others
cold.I havent tried forcing water in from the drain end as yet. If I
do that it will be me in the roof with the cloths, as the friend(my
wife)will be with the hose. I do not want to think about it the other
way around.It will be Wednesday before I can try it.
Thanks again, I'll report back.
|
Clarification of Question by
raefa-ga
on
14 Jan 2005 08:57 PST
Hi Guzzi, Tried the backfill, but no joy. Seemed to fill very quickly,
which surprised me, so I am wondering if everything had drained
completely. I did open vent in roof to allow air in to avoid a vacuum
and left it a couple of hours to dribble.WIl try it again, tomorrow
Saturday.Eased nuts at joints in roof and all spurtedwater.I was
hoping one would be dry.
|
Clarification of Question by
raefa-ga
on
20 Jan 2005 06:47 PST
Hi Guzzi, Still draining and bleeding and swearing and still no hot
rad's. Since I last reported, I have had floorboards up and drained
system from there, as there was still water in, even after drain plug
had stopped running.I have fitted an extra bleed valve in main pipe in
roof(now has one in flow and one in return), which definitely had air
in as I cut through before draining, very clear gasp heard and some
seconds before water leaked. Followed by very quick descent to outside
drain plug!! Removed paddle from isolator in roof as pipe on each side
was not same temp', so wondered if it was not fully opening and
restricting flow. Pipe both sides now equal temp'. Boiler fires for
about 4 minutes and then cuts out and it is about 30 minutes before it
fires again.
Everytime I bleed in roof, valves and pump, I get air. No air coming
from any radiators now.If I bleed one radiator into a bucket it will
eventually get hot, but starts to cool as soon as I close bleed valve.
Have done this on several different radiators with same result. Flow
and return pipes in roof get hot.
Dont know whether it has any bearing but this is a bungalow. I havent
used compressed air suggestion as I do not have it, but all radiators
bleed quite freely, but some better than others.
|
Clarification of Question by
raefa-ga
on
21 Jan 2005 03:15 PST
Hi Guzzi, I have had the pump off to clean ports and even reversed it
to see if it would shift whatever it is, but I wont do that again as I
thought the place was going up any minute, all pipes rattling, boiler
making strange noises, I got the impression that you dont do that!!
Pipes are 22mm up and down to ground floor and then 15mm to each radiator.
Have tried boiler on max' but it just shuts down the same.
I feel that the pump is OK as the return from ground floor back into
roof gets hot, so assume water must be circulating.
Just awaiting draining and then going to do yet another back fill.
Have installed a on/off valve in expansion pipe as last time water
eventually ran up it and into header tank. First I knew was when
overflow started running.
Watch this space for the next episode.
|
Clarification of Question by
raefa-ga
on
21 Jan 2005 08:40 PST
Hi Guzzi, Back filled, bled etc, no change. Drained again,incuding
boiler, closed all valves, refilled, bled as per your sequence, then
spent 1 1/2 hours sitting in roof just bleeding 5 valves and the pump
in turn. Loads of air out of each and then eventually it got quieter
and all the pipes were hot and for once I could still hear the boiler
firing.Went down with everything crossed and radiators were hot!!!!!!!
Its been a long week and a lot of wasted time, but many thanks for
your advice and support. Have a good nights sleep and a drink on me.
Kind regards, Raefa.(childhood nickname)
|