what is the amperage rating for a 3 phase 6 ton,480 volt,hvac unit with 9kw electric heat strips.thanks |
|
| There is no answer at this time. |
|
| Subject:
Re: electrical help
From: sume-ga on 21 Jan 2005 21:12 PST |
can you clarify the question some more is it Air conditioner ? |
| Subject:
Re: electrical help
From: theshad0w-ga on 22 Jan 2005 13:28 PST |
http://www.meiersupply.com/specs/ukka036-073.pdf Page 9 implies that 6-ton is 21.1 KW, which for 3-phase 480 volt would be 14.7 amperes. Going further down in the reference, the current requirement for the larger 480 volt units is 15 amperes, which matches the above calculation. |