Answered By: hedgie-ga on 27 Jul 2005 02:20 PDT |
on 24 Jul 2005 11:41 PDT you ask: So connecting this heater directly to 110v .. would be ok? Answer is yes. As long as heating element is just a resistor (i.e. just connecting wires and the heating coil, no electronics atd) it can be safely connected to lower voltage then nominal. What is shown on the apliance as 'wired for' - the nominal voltage - is actually the maximal voltage the appliance can handle. At any voltage applied, the output is V*V/R where V is applied voltage and R is resistance of the heating coil. If nominal voltage 220V would produce output 4.8 kW then R of the heater is 10 Ohms ( you can type into google: (220 V * 220V)/ 4.8 kW to get that result) ( axel_wg-ga on july 13 was using 120 V to get about 3 Ohms) Therefore, if you apply 120V, your heat production will be ((129 V) * (120 V)) / (10 ohm) = 1 548 watts and it will draw current of (120 volts) / (10 ohm) = 12 amperes The 50 amp breaker would work, but use 15 amp, as it is sufficient and safer Hedgie |
|
Subject:
Re: Reducing the power drain from a heating element
From: simon2wright-ga on 12 Jul 2005 13:07 PDT |
The best way of reducing the current used by a heating element is to reduce the voltage going to it, by means of a step-down transformer or switch-mode electronic regulator. |
Subject:
Re: Reducing the power drain from a heating element
From: axel_wg-ga on 13 Jul 2005 16:38 PDT |
simon2wright-ga is correct. To be more precise you have to reduce the voltage to your 5.5 kw element to 84V to get a ~2714W heat output. Your element has a hot resistance of about 2.6 Ohm. 84V divided by 2.6 = 32.3 Amps times 84V = 2713 Watts. If you find a 120V-36V, 35A (~1.5kva,~$150) transformer and hook up the 36V winding reverse to 120V you get 84V. A good electrical contractor should be able to help you connect it. This is a faily low loss solution. Electronic regulators are very expensive unless you find some used ones, good luck. |
Subject:
Re: Reducing the power drain from a heating element
From: biodiesel_bri-ga on 24 Jul 2005 11:41 PDT |
So connecting this heater directly to 110v with a 50amp breaker (with appropriate gauge wire) would be ok? The heater wants 5.5kw at 220v right now, not 110. |