| Subject:
Electrical wiring
Category: Miscellaneous Asked by: gush-ga List Price: $2.00 |
Posted:
10 Mar 2006 18:28 PST
Expires: 09 Apr 2006 19:28 PDT Question ID: 705953 |
is it safe to wire two runs of 12/3 romex in parallel for a 30 amp subpanel in my shop? Ideally, I would use 10/3, but I have lots of extra 12/3, and nothing to use it on. Thanks! Also, would it be up to NEC code (in California if it matters)? |
|
| There is no answer at this time. |
|
| Subject:
Re: Electrical wiring
From: nitro77-ga on 17 Mar 2006 15:38 PST |
Safe/ sure,as long as the wire fits into the connectors.I'm not familar with the cal codes but they surely will allow this set up.As an added reason for them to approve this unstandard style try wraping both runs together.Black tape will do wonders here. |
| Subject:
Re: Electrical wiring
From: ndjimmyd-ga on 24 Mar 2006 14:27 PST |
What you described would actually be in violation of the NEC (National Electric Code). The NEC allows only conductors of size 1/0 AWG and larger to be wired in parallel (with a few very limited exceptions that you would not fall under). #12 wire would be too small to be legally run in parallel. The relevant code reference is NEC article 310.4. The NEC code would apply in California. If a building inspector is reviewing this installation, they would likely make you use the #10 wire. |
If you feel that you have found inappropriate content, please let us know by emailing us at answers-support@google.com with the question ID listed above. Thank you. |