Question  
Subject: Steel Beam Sizing
Category: Science > Physics
Asked by: josephc68-ga
List Price: $10.00
Posted: 28 Oct 2006 12:57 PDT
Expires: 27 Nov 2006 11:57 PST
Question ID: 777843
I am doing some reinforcement in my house to compensate for some poor
building practices.  I need to support a 2nd floor and attic load
without exceeding the depth of my joists, 7 1/4".  I used an
engineered lumber program to compute my loads but do not know how to
convert this load information to size a steel beam.  I am pretty sure
that a W6x25 would carry the load but would like this confirmed and to
see the math behind this.

Deflection Criteria: Specified(LL:L/360,TL:L/240). 

Load Group: Primary Load Group
                                   _________________
                                    ^  14' 11.50"  ^ 
Max. Vertical Reaction Total (lbs) 6473          6473
Max. Vertical Reaction Live (lbs)  4550          4550
Required Bearing Length in       2.47(W)         2.47(S)
Max. Unbraced Length (in)                35         

    Loading on all spans, LDF = 0.90 , 1.0 Dead 
Shear at Support (lbs)                1569   -1569  
Max Shear at Support (lbs)            1896   -1896  
Member Reaction (lbs)              1896          1896
Support Reaction (lbs)             1923          1923
Moment (Ft-Lbs)                          7091       

Loading on all spans, LDF = 1.00 , 1.0 Dead + 1.0 Floor 
Shear at Support (lbs)                5281   -5281  
Max Shear at Support (lbs)            6384   -6384  
Member Reaction (lbs)              6384          6384
Support Reaction (lbs)             6473          6473
Moment (Ft-Lbs)                          23872      
Live Deflection (in)                     0.486      
Total Deflection (in)                    0.691

Request for Question Clarification by redhoss-ga on 28 Oct 2006 16:03 PDT
Just out of curiosity, what were the loads that you used to get these
results. I can answer your question.
Answer  
Subject: Re: Steel Beam Sizing
Answered By: redhoss-ga on 30 Oct 2006 08:14 PST
 
Okay josephc68, I guess you don't want to tell me how you got your
numbers. We will just use your numbers and go ahead.

The maximum bending moment is:

M = Rx x L/2 = 6473 x 89.75 = 580,952 in-lbs

The required section modulus is:

S = M/allowable stress = 580,952/(36,000 x .55) = 29.34 in^3

The allowable deflection is L/360 = 179.5/360 = 0.5 in

Using this deflection to calculate the required moment of inertia:

Where P = 2 x Rx = 12,946 lb
      E is the modulus of elasticity of steel = 30,000,000 psi
      
I = PL^3/48ED = 12,946 (179.5^3)/48 (30,000,000)(0.5) = 104 in^4

The properties for a W6x25 are:
S = 16.7 in^3
I = 53.3 in^4

So, you see that the W6x25 is not adequate. It looks like your best
choice would be a W8x40 with S = 35.5 and I = 146.

Look this over and if you have something else you would like to try
please ask for a clarification.

Redhoss

Request for Answer Clarification by josephc68-ga on 30 Oct 2006 11:10 PST
Sorry Redhoss, I didn't get my email notification that there was an
answer waiting for me.  For simplicity my loads are a 10' tributary
with 30 psf live load and 12 psf dead load.  Do I have any other
options in terms of a steel beam that would be less than a 2x8 (7.25")
in height?

In what sense is the W6x25 inadequate, deflection?  The reason I ask
is that I found a table online that shows the W6x25 can support 652
lb/ft over a 16' span.

Thanks.

Clarification of Answer by redhoss-ga on 30 Oct 2006 14:03 PST
I wish that you had started with the info that you state in your
clarification request. If you take your new numbers here is what we
have:

w (load in lbs. per foot) = 42 psf x 10 = 420 lb/ft

So, the end reactions would be:

Rx = 420 x 14.958 / 2 = 3,141 lbs.

This is less that half the 6,473 number that your "engineered lumber
program" gave you. I don't know what went wrong, but it yielded some
bogus numbers. Here is a re-calculation using the correct numbers:

The maximum bending moment is:

M = Rx x L/2 = 3,141  x 89.75 = 281,905 in-lbs

The required section modulus is:

S = M/allowable stress = 281,905/(36,000 x .55) = 14.24 in^3

The allowable deflection is L/360 = 179.5/360 = 0.5 in

Using this deflection to calculate the required moment of inertia:

Where P = 2 x Rx = 6,282 lb
      E is the modulus of elasticity of steel = 30,000,000 psi
      
I = PL^3/48ED = 6,282 (179.5^3)/48 (30,000,000)(0.5) = 50.46 in^4

Now the W6x25 looks just fine. Good choice.
Comments  
Subject: Re: Steel Beam Sizing - josephc68-ga
From: poodleheadmikey-ga on 18 Nov 2006 19:37 PST
 
Joe,

I just wanted to gently point out that if it ever comes around again
that you are restricted by height and so cannot get the load rating
you need - just use two beams side-by-side.  Even without joining
plates they are fairly close to being double the strength of one beam.

PHM
----------

Important Disclaimer: Answers and comments provided on Google Answers are general information, and are not intended to substitute for informed professional medical, psychiatric, psychological, tax, legal, investment, accounting, or other professional advice. Google does not endorse, and expressly disclaims liability for any product, manufacturer, distributor, service or service provider mentioned or any opinion expressed in answers or comments. Please read carefully the Google Answers Terms of Service.